I would ask you: ¿Can the OPC Server for Siemens S7 read LREAL Values? I have to read it from S7 1200 PLC's, but as far as I've read in your manual, I haven't found this capability...
¿How can I deal with LREAL Values? (NOT REAL)
Thank you,
Offline Manibhushanreddy P  
#2 Posted : Thursday, February 8, 2018 10:21:05 PM(UTC)
Manibhushanreddy P

Rank: Newbie

Joined: 3/23/2016(UTC)
Posts: 5

Hi

Thank you for contacting MatrikonOPC Support.

I believe you are talking about LONG or DINT (Data block variable which represents a signed decimal integer, stored in four bytes.) data type when you say LREAL. So you could use below syntax to fetch LONG type values from PLC.

DBn:DINT:x
n is the data block number
x is the DINT offset
e.g.: DB1:DINT:10 accesses a DINT at offset 10 from data block # 1

If you have any further questions you may refer to OPC Data Items section in user manual where all the PLC data blocks explained with their syntax.

Hope this helps.

Mani